8B, 9B) - If gate opening is activated (motor turning in the opposite direction), press PROG to correct the
direction and activate closing.
10, 11) - On reaching the limit stop, the motor stops and automatically restarts in opening.
12) - On completion of opening, the motor stops and the control unit starts to count the pause time.
13) - Once the required pause interval has elapsed, press the S/S button and the motor starts closing.
14) - On reaching the closing limit stop, the motor stops. Led LD1 switches off at the end of the programming
procedure.
PROGRAMMABLE DECELERATION POINT (Excett T124RAP4 and T124RAP6)
With the T124 unit, the point at which gate travel starts to decelerate can be programmed.
To set the deceleration point, proceed as follows:
- during the opening phase in the self-learning cycle (i.e. after point 11 of the "WORK AND PAUSE TIME
PROGRAMMING" procedure has been carried out), press the "PP" button to set the starting point for the
deceleration phase during opening. The gate will stop for a moment to signal the deceleration point
programming is complete.
- during the closing phase of the self-learning cycle (i.e. after completing point 13 of the "WORK AND PAUSE
TIME PROGRAMMING" procedure ), press the "PP" button to set the starting point for the deceleration phase
during closing. The gate will stop for a moment to signal the deceleration point programming is complete.
NOTES:
1) Deceleration point programming is not compulsory. If the point is not programmed, the control unit activates
travel with deceleration at a preset point.
2) The two preset deceleration points (opening and closing) are not connected in any way.
3) For sliding gate models, the preset deceleration point is designed to meet the relative standards in force. You
should only use the deceleration point programming function if the gate decelerates too close to the end stop
(it should have decelerated completely when positioned 50 cm from the end stop, to reduce impact in the
event of obstructions).
PEDESTRIAN OPENING PROGRAMMING
With the "factory" set programming, the pedestrian control opens the gate by approx. 1/1.5m.
To increase or decrease this distance, proceed as follows:
- repeat from point 1 through to 5 of "working and pause time programming";
- press the Pedestrian button (wild input with dipswitches 3 and 4 ON) or transmit with the second radio channel
(also see section "plug-in receiver" page 38);
- the gate starts to close;
- when the gate arrives at the limit switch the motor stops and then automatically restarts in the direction for
opening;
- when the gate is sufficiently open, press the pedestrian button again;
- the gate closes and exit from programming is automatic.